Issue of the length of the factory building: Are there any specific regulations regarding the length? What are the main factors to consider, etc.? Thank you!
Reply #22010-08-01
It should be checked; for concrete structures, the limit is ≤60m, and for steel structures it is ≤120m – the specification shall determine this.
Reply #32010-08-01
The answer above is very good. I learned it! ~
Reply #42010-08-01
The answer on the 2nd floor is correct. For the specific structure, you should check the relevant specifications!
Reply #52010-08-01
Everyone discussed it very well; I learned a lot!
Reply #62010-08-03
I still feel there are doubts! The length of factory building frames I have seen, with concrete frames combined with steel structural floors, has reached 90 meters. I mainly want to ask everyone whether it’s possible to extend the factory building any further, and if there are any regulations regarding its length
Reply #72010-08-04
The external dimensions of structural elements should be designed based on practical functions and manufacturing requirements; structural measures can be adopted when the dimensions exceed a certain limit. For example, if the size is too large, expansion joints can be installed. Set settlement joints at different heights.
Reply #82015-10-24
The length of the structure shall be determined according to the project requirements. Mainly consider emergency exit routes and fire separation distances.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.