How should a layperson choose an air switch when looking to purchase one?

2010-08-14View Original

Thread Content

I have an inverter with a power rating of 3.7 kW. I want to add an air switch for easier control. I need help from everyone: 1. What size air switch should be chosen? 2. What gauge of wire is suitable for the wiring between the switch and the frequency converter? 3. By the way, when choosing an air switch, is there any relationship between the rated current of the air switch and the power of the equipment it is used to control? Thank you all
Reply #22010-08-14
For the circuit breaker, it’s better to choose 20A; if you want extra safety, go with 40A. Since the distance between the circuit breaker and the inverter is not too great, 4*2.5 wires are sufficient.
Reply #32010-08-14
The current is not high, around 7A; a circuit breaker with a capacity of 25A or 32A will work fine. It is recommended to use 4-square millimeter wires
Reply #42010-08-14
I think a 16A circuit breaker should be sufficient, after all, the load is an inverter rather than a motor directly, and the rated current of the inverter is around 7A. Since the operating current is low, using 2.5 square millimeter wires should not be a problem. It is easier to wire compared to 4 square.
Reply #52010-08-16
I = P/U/1.732/0.8; the rated current is thus around 7A. A 16A circuit breaker is sufficient, along with 4*2.5 mm² wires – for reference only
Reply #62010-08-22
Each switch has its own set of parameter settings; depending on the chosen settings, it can be set to 16A or 20A. A 4*2.5 wire gauge is suitable for short distances, while a 4-square wire gauge is appropriate for longer distances. The wire gauge should be 1-1.5 times larger than that required by the load

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.