Distance between pipes installed on the pipe tray and electrical and instrumentation cable trays

2010-08-25View Original

Thread Content

The bottom layer of the double-layer pipe gallery is 3.5m thick, while the upper layer is 5.5m thick. There are pumps located below the gallery; in this case, should the electrical cable trays be installed on the upper layer or the lower layer? What is an appropriate distance between electrical cable trays, instrument cable trays, and pipes? (Is it greater than or equal to 500 cm?) )
Reply #22010-08-25
The electrical cable trays should be installed on the upper layer. Instrumentation and electrical cables should not be arranged together; the minimum distance between them should be greater than 1000 mm. It is advisable that the clear distance between electrical cable trays, instrument cable trays, and pipes be greater than 300. For your reference.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.