Regarding the calibration of the liquid level measurement range, friends, come and take a look to see if what I’ve done is correct

2010-09-01View Original

Thread Content

The single-flange pressure level gauge from E+H – I’m not sure why, but the product I received differs somewhat from what I had ordered. So some adjustments were made; everyone, does it look right? My situation is as follows: the level gauge is installed at a distance of 0.3 meters from the bottom of the tank, with the tank’s height being 9.75 meters. The specific gravity of the medium in question is 1.83, and the actual measurement distance is 9.45 meters. The level gauge purchased has a range of 0–100 KPA; it was calibrated using water as a reference, where 10 meters of water corresponds to 100 KPA. Based on the specific gravity of 1.83 for the medium in use, it can be calculated that 5.46 meters of this medium correspond to 100 KPA. Therefore, the pressure at the full measurement range of 9.45 meters would be 173 KPA. Should I adjust the range of the level gauge to 0–173 KPA? Meanwhile, the level gauge on the DCS system has a range of 0.3–9.75 meters. Is this approach correct?
Reply #22010-09-01
Measure the distance from the transmitter to the flange. I don’t know whether the level gauge you purchased came with a flange and a capillary; if it does come with a capillary, then you need to determine the density of the filling liquid inside that capillary in order to calculate the amount of migration. Alternatively, when the container is empty, you can simply read the value shown on the level gauge and use that value as the amount of migration, and then adjust for positive migration.
Reply #32010-09-02
Without capillaries, am I doing this correctly?
Reply #42010-09-02
Just do the migration? No need to change the range?
Reply #52010-09-02
That’s right, it’s possible to do that. However, the zero point of E+H tends to fluctuate, so pay attention to its maintenance
Reply #62010-09-02
The range of the level gauge is 0~169KPA
Reply #72010-09-03
Reply to 6# heartoking: May I ask how you determined this range of 0~169KPA? Thank you
Reply #82010-09-03
Range = 9.45*1830*9.8 = 169 kPa. The DCS range can be set between 0 and 9.45; the 0.3 meters below the measurement point constitutes the process reserve level, which is the dead zone for instrument measurement.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.