The power supply of Rosemount 1700 is 24V DC and cannot be used.

2010-09-17View Original

Thread Content

1700 series, analog output. Use the calibrator to power 24V and connect it to pins 9 and 10 of the flow meter, but only 2 small lights flash on the flow meter and there is no display on the display. Is the power supply insufficient? Does it have to be 220V AC? ? ? Flowmeter 1700 series, integrated. DCS requires a 4-20m A 1,2 point signal from the flow meter.
Reply #22010-09-17
Sorry for posting this post to insult all seniors. I didn't find the manual (on CD) beforehand. After reading the manual, it seems that the 24V power supply needs to be preheated. The power consumption is relatively large, or something. In short, it takes about ten minutes to preheat. I'm so sorry. This is my first time using it, please understand.
Reply #32010-09-17
The main reason is that although the test instrument can reach 24V voltage, its power is not enough to carry some equipment on site. We have encountered such a problem before. Let’s see if you have a PLC cabinet or other active power supply.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.