Our factory uses Honeywell EPKS210 and C200 controllers; we have been using them for 5 years. During that time, many additional points were added, so there aren’t likely many CM points left. The leader plans to add more card slots, so they asked me to count the remaining quantity of points. Dear sea friends, is there any way to check the remaining point count at once?
Reply #22010-09-19
Open Control Builder, select Monitor under IOLINK, find each IO card. Right-click on each IO card and choose “Module Properties”. Under the “Status Data” tab, you can see the status of each channel. Generally, the name of each channel will be changed to match its identifier; in other words, the names will still be things like “AICHANNEL_1” and “DICHANNEL_1”, indicating that those channels are not yet in use
Reply #32010-09-19
My company also uses the R210 system; we can discuss this together. My QQ number is 289429881, with the username Haichuan
Reply #42010-09-20
Thank you for your answer. I know how to do this method as well; I’m just wondering if there are any other ways to quickly find out the quantity and types of various cards remaining in the system
Reply #52010-09-20
Many systems should provide, in the engineer interface, a way to directly view the usage and settings of all card channels
Reply #62010-09-20
Apart from the method on the 2nd floor, I haven’t found any other more convenient one at the moment.
Reply #72010-11-09
What was said on the second floor is completely correct! This is how it’s checked in the software; the address list used for maintenance is very important. It contains information that has been manually stored, and there should be records in it as well, and they’re quite clear too
Reply #82010-11-09
The second floor has covered it very comprehensively; this is the only way to proceed
Reply #92010-12-18
Find the authorized page on the operation station to see the points used; then calculate the total number of channels by using the total number of cards, and subtracting that value gives the remaining amount.
Reply #102011-02-17
Hello, do you have any information on the Honeywell PKS R210? If you have any, please get in touch with me. Thank you. My QQ number is 289429881

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.