How should the PLC cabinet be grounded?

2010-09-23View Original

Thread Content

Do all the electrical components of the cabinet and the UPS’s electrical grounding simply need to be connected directly to the cabinet? The cabinet is welded to the steel channel below. Channel steel is generally used for grounding
Reply #22010-09-24
Is your channel steel grounded? If the channel steel is connected to the ground, you can do it just like this!
Reply #32010-09-24
How is electrical grounding handled in ordinary PLC cabinets?
Reply #42010-09-24
First, the construction drawings should be checked to confirm that the channel steel is indeed connected to the grounding grid; Secondly, after the electrical components are properly connected, it is also necessary to ensure that the ground resistance is less than 3 ohms ; Meeting these two requirements basically confirms that the equipment is properly grounded.
Reply #52010-09-24
For ordinary PLC cabinets, the electrical grounding can be connected to the electrical protection ground.
Reply #62010-09-24
In my opinion, the grounding of a PLC should be floating grounding, and it should not be connected to the electrical common ground
Reply #72010-09-24
Oh, is it usually the channel steel under the PLC cabinet that is connected to the grounding grid? Is this the case for general electrical grounding? Should ground wires be drawn from each PLC cabinet separately to a centralized electrical grounding device?
Reply #82010-09-25
The grounding of PLC cabinets should be separated from that of instruments and electrical equipment; UPS units are generally not grounded in order to improve reliability. Additionally, generally, the electrical ground resistance should be less than 4 ohms
Reply #92010-09-27
The shield ground and the protective ground are grounded separately.
Reply #102010-09-28
It is best to perform grounding separately, especially in the presence of interference sources such as frequency converters.
Reply #112010-09-28
Generally, the grounding for DCS instruments is separate and cannot be shared with that of electrical systems

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.