The unit did not trigger any alarms; why did the safety valve activate?

2010-10-08View Original

Thread Content

When the refrigeration unit was started, no alarm was triggered for the high discharge pressure; however, for some reason the safety valve of the condenser opened, resulting in a large amount of Freon and oil leaking out. I would appreciate it if any expert could help explain this phenomenon. Thank you!
Reply #22010-10-09
It’s possible that the setting for the safety valve’s operating pressure is incorrect, causing it to activate before reaching that pressure; it’s best to consult the manufacturer. Waiting for the expert to make corrections!
Reply #32010-10-09
Possible causes: 1. Faulty exhaust pressure sensor. 2. Incorrect startup logic (such as delayed detection of exhaust pressure). 3. Faulty safety valve

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.