Axial flow fan static blade adjustment mechanism

2010-10-09View Original

Thread Content

The static vane control mechanism of the catalytic axial flow fan has failed; as part of the unit’s self-protection system, the main fan cannot have its static vanes controlled automatically before it is activated, but now it is possible to control them. The unit has been switched to automatic operation, and the static blades should be capable of being adjusted; however, they can no longer be adjusted and have been set directly to 22 degrees. Everything is reversed. Have you encountered this situation before? Please help analyze it – it’s an emergency
Reply #22010-10-10
1. Check if the logic is correct? 2. Check if the forced point has been restored? 3. Check the safe operation status or whether there are interlock signals for the main air supply
Reply #32010-10-12
I’ve found the cause; there’s a problem with the settings of the stator actuator

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.