2010-10-13View Original

Thread Content

What is the fire separation distance between storage tanks for Class A and Class B flammable liquids? Should it be in accordance with Note 5 of Article 4.2.1 of the Building Code, or is it sufficient to leave a 7-m fire access lane as specified in the Chemical Industry Code? Also, can underground tank areas be arranged in groups? What should the fire separation distance be if it is possible to have one?
Reply #22010-10-13
Brief explanation: First, it is necessary to establish the standards for project execution; the same project cannot follow inconsistent standards at the same time. There are many differences between construction regulations and petrochemical industry regulations. The concepts of tank groups and tank areas are also different. Buried storage tanks do not have the concept of grouping, while ground storage tanks are grouped in order to establish fire dikes.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.