Pressure difference Flow rate

2010-10-14View Original

Thread Content

There is a KV differential pressure flow meter; the pressure difference gauge suddenly stopped showing readings. Upon inspection, the supply voltage was 18V, but it dropped to 5V once connected to the gauge, with a measured current of 10 milliamps. Can these data be used to determine that the gauge is damaged, or that there is a problem with the module inside it?
Reply #22010-10-14
It’s abnormal when only 5V is available after connecting it to the meter; at this voltage level, the transmitter definitely cannot function properly. Try connecting a separate 24V supply to the transmitter to see if it works properly. If the transmitter is working properly, then it’s a problem with the secondary meter or the host computer. If the transmitter does not display anything even when powered by 24V separately, then it is definitely a fault with the transmitter. The original poster, give it a try
Reply #32010-10-14
Check whether there is a ground connection or a branch circuit in the power supply circuit that is causing the voltage to drop

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.