Power supply for the valve position transmitter

2010-10-15View Original

Thread Content

For pneumatic control valves, is the power supply for the valve transmitter the same as that for the positioner?
Reply #22010-10-15
Do you mean the valve position transmitter?
Reply #32010-10-15
Reply 2# KUIK Yes
Reply #42010-10-18
Yes, it should be an AI signal with 24VDC. It’s the same wire as that of ordinary pressure transmitters.
Reply #52013-12-28
For the baffle on that heating furnace, the valve position transmitter is an AI point, while the positioner is an AO point. I would like to ask whether they are both fed into the SIS or the DCS ?
Reply #62013-12-28
Analyze each specific issue; every valve transmitter and position transmitter is different. Find a manual or provide me with the model number
Reply #72013-12-28
1. Valve position transmitter: two-wire active signal, outputs 4-20mA. 2. Positioner with valve position feedback: the valve position sensing unit is also an independent two-wire active signal. As an analog signal, the valve position signal is rarely used as a interlock condition in SIS; it is usually utilized in DCS as a reference for displaying valve position changes.
Reply #82013-12-28
It’s not a two-wire system for the entire length; it’s a transmitter with separate power supply lines.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.