Is it necessary to have two separate systems for the high liquid level alarm in hazardous chemical storage tanks?

2010-10-21View Original

Thread Content

Dear technicians, I’ve heard that for high liquid level alarms in liquid chemical storage tanks, two independent systems are required – namely a level gauge (currently radar level gauges are used for high level alarms) and a fork-type alarm. **Is this indeed a mandatory requirement per the standards?** Is it sufficient to use only the high-level alarm of a radar level gauge? So there’s no need for a tuning fork-based high liquid level alarm?
Reply #22010-10-21
I don’t think so. Here, our liquefied gas tanks use only one servo level gauge in accordance with the new standards for high-level monitoring, while for light hydrocarbons, fork-type level gauges are used (previously, both types used radar level gauges, but the errors were quite large, so they were replaced)
Reply #32010-10-22
Are there any standards or guidelines in this area? ? Please provide it
Reply #42010-10-25
There is no mandatory requirement; it only states that a high liquid level alarm and a very high liquid level alarm are needed.
Reply #52010-10-25
There is no mandatory requirement; it only states that a high liquid level alarm and a very high liquid level alarm are needed.
Reply #62010-10-25
From a security perspective, two separate systems should be used!
Reply #72010-10-25
Are the high liquid level alarm and the very high liquid level alarm two separate systems? ? ? ? Are there any regulations in this regard?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.