2010-11-08View Original

Thread Content

How to debug this valve positioner LOGIC 500 on-site? There is a round cover; when it is opened, there is a QUICK CALC button inside, along with a button that goes upward and one that goes downward. When I send a 4–20MA signal, the valve does not move and the lights inside do not light up either. I would appreciate some guidance from experts.
Reply #22010-11-08
This might be a British type of valve; I’ve never used this kind of valve before.
Reply #32010-11-08
Are you trying to verify the valve or something else? If you want to do self-tuning, you can press the quick calibration button for three seconds and it will start
Reply #42010-11-08
http://www.flowserve.com/Products/Automation/Positioners-Digital
Reply #52013-05-25
What do landlords in English-speaking countries think? Is there any content in Chinese?
Reply #62013-05-25
The QUICK (fast button) doesn’t work; it’s not for verification

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.