I’ve been in this field for not long, and I’m facing a problem now; I hope those with more experience can help me out! I have a nitrogen storage tank with a DN5000 diameter and a straight section length of 7200. There is currently one safety valve with a DN50 size. I initially planned to place this safety valve on top of the upper head, but the client disagreed; they want it to be installed on the cylinder wall at a distance of 1500 from the straight edge of the lower head. I was wondering if any standards specify the location where safety valves should be placed, so that I can provide a proper explanation! Thank you first~
Everything I’ve seen is at the end cap or on top of the equipment; check that
If it is a gas storage vessel, the safety valve is generally installed in a place that is not easily accessible to people; it should also be possible to install it on the cylinder at a distance of 1500 from the straight edge of the lower head
The phases must be consistent and belong to the same pressure system; the pressure drop at the inlet and outlet during startup must meet the requirements for installing safety valves. It can even be installed on the inlet and outlet pipelines of the container.
There seems to be a standard requiring that safety valves be installed vertically at the top of the container; I can’t remember the specifics exactly, so I’ll check it out
The requirements for installing safety valves are as follows: 1. Safety valves should be installed vertically, and they should be placed in the gas phase space above the liquid level of the pressure vessel, or on a pipe connected to the gas phase space of the pressure vessel. 2. The cross-sectional area of the connecting fitting between the pressure vessel and the safety valve must not be smaller than that of the safety valve’s inlet; the piping used for connection should be as short and straight as possible. 3. The installation location of the safety valve should facilitate inspection and maintenance. . . . . . . . .