Seeking advice on vortex flowmeters

2010-11-12View Original

Thread Content

This post was last edited by lant on 2010-11-12 at 18:25. Regarding the Pulse Width Limit function of the Coriolis vortex flowmeter, the options are YES or NO. What impact does this have on the operation of the vortex flowmeter, and when should it be enabled? What does RangeP mean? In my factory, the value for this parameter is 0.001 PULS/T (with a K coefficient of 318 P per cubic meter). What does this mean? I would like to ask the teachers, thank you. The corresponding explanations are as follows:
**Fct. 1.3.0 PULSE O/P**: This submenu groups functions related to Pulse output.
**Fct. 1.3.1 FUNCTION P Pulse output**: Select YES to enable Pulse output as per functions Fct. 1.3.2 to Fct. 1.3.3; selecting NO disables Pulse output (0 Hz).
**Fct. 1.3.2 RANGE P Pulse output range value**: Enter a value here for the number of pulses required per unit volume/mass. This value must always be set after the max flow value Fct. 1.1.2 has been set. For example, for a value of 0.1 Kg, 10 pulses per Kg means 1 pulse per 0.1 Kg. Pulse output programming is independent of the maximum flow rate. The various unit options for this range are listed below:
- For volumetric flow: • PULSE/m3 • PULS/litre • PULS/ft3 • PULS/cft • PULS/cuft • PULS/US.Gal • PULS/UK.Gal
- For normalized volumetric flow: • PUL./Norm.m3 • PULS/Norm.L • PULS/Sft3 • PULS/Scft
- For mass flow: • PULS/kg • PULS/t • PULS/Lb
**LIMITS**: (0 TO 0.5 Hz) / Q, where Q 100% represents the flow rate in volume or mass units per second.
**Fct 1.3.3 P. WIDTH.LIM pulse width**: You can limit the duration of the active pulse width of the Pulse output. Options are:
- YES: Limits the pulse width to 250 mSec.
- NO: Keeps the Pulse output at a 50% duty cycle. This function helps to minimize overheating of the totalizer coils.
Reply #22010-11-12
Pulse Width Limit is referred to as the pulse width restriction, and it can be set to 250ms. 318P per cubic meter means that 318 pulses represent 1 cubic meter. I’m not sure if this understanding is correct
Reply #32010-11-14
Reply to 2# shakic: For the first question, there are only two options – open or closed. From what I can understand in English, this setting helps to protect the coil. The second question is that, according to the instructions, pulse limitation is the ratio of a certain frequency to full scale. I’m not sure if that’s correct?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.