What should the insulation resistance of the instrument signal wires to ground be to not affect measurements?

2010-11-25View Original

Thread Content

During work today, an abnormality was detected with one instrument; the insulation resistance between the signal wires and the conduit was 22 megohms. There was disagreement among those present regarding this issue. I would like to ask the experts here: what should the insulation resistance be between the instrument’s signal wires and the conduit so as not to affect measurements?
Reply #22010-11-25
The current signal should generally be infinite; I haven’t tried to find out what the minimum value could be. The insulation resistance of thermocouple signals can be quite low – some devices can still function with values in the range of a few megohms. As long as it works properly when tested with a signal generator, that’s fine!
Reply #32010-11-25
The insulation resistance of the instrument signal wires relative to ground should be 4 ohms without any impact on the measurements
Reply #42010-11-25
4 ohms? That’s impossible! ! !
Reply #52010-11-25
For the one on the 3rd floor, the 4 ohms you’re referring to is likely the resistance of the instrument signal ground, not the instrument signal wire.
Reply #62010-11-25
Theoretically, it seems that a value greater than 20 megohms is sufficient, but in practice, the values you have measured indicate that the grounding of your signal lines is poor.
Reply #72010-11-25
Theoretically, it should be infinite; if it’s 20 megohms, then it should work.
Reply #82010-11-25
An insulation resistance of 22 megohms should not present any problems. Abnormal readings from instruments are generally not related to insulation resistance; they are usually caused by interference or poor shielding. It is possible to check whether the shielding grounding is secure and whether the grounding resistance meets the required standards – generally, the grounding resistance should be less than 4 ohms~~
Reply #92010-11-25
Under normal circumstances, does insulation resistance also affect the detection? Incredible.
Reply #102010-11-26
22M ohms should be fine; I also tested it on-site, and most values were in the range of seventy to eighty megohms

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.