2010-12-15View Original

Thread Content

After taking the square root of the differential pressure transmitter, the milliampere signal is sent to the DCS. According to the formula: differential pressure = constant * flow rate squared * density. But the actual density is 1.2, not 1.5, which is the density specified in the transmitter formula. If the square root of 1.5/1.2 equals a constant, then is the actual flow rate that constant multiple of the flow rate displayed by the DCS? If not, what is the actual volumetric flow rate?
Reply #22010-12-15
This post was last edited by wxz_9999 on 2010-12-15 at 15:50. Without temperature and pressure compensation, the value displayed on your DCS corresponds to the flow rate based on the pressure and temperature values given in the orifice plate calculation sheet; in other words, it represents the volume at a density of 1.5. You can find the corresponding temperature and pressure for a density of 1.2 using a density table, and then perform the conversion using the formula P1V1/T1=P2V2/T2. I think when calculating volumetric flow rate, it should not be related to density, but rather to temperature and pressure.
Reply #32010-12-15
Reply to 2# wxz_9999: But the formula provided by the manufacturer is related to density; it refers to the flow rate of a liquid that is quite viscous.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.