2010-12-25View Original

Thread Content

Is the interlock activated when starting up the heating furnace? When should it be put into use? (It’s best to specify exactly which step triggers the interlock mechanism, as using it at the wrong time can either prevent the furnace from starting up or pose a serious risk.) Thank you
Reply #22010-12-26
It is generally put into use only after ignition and heating are complete and normal production begins. During the furnace heating process, manual control is used for a gradual increase in temperature; if interlocks are activated at this time, it becomes impossible to switch to a favorable safe state in a timely and effective manner should any problems arise.
Reply #32011-01-02
I haven’t put the four-in-one furnace interlocks into use; they weren’t activated due to external factors. The system operates smoothly, with only alarms set up. There are some interlocks that should be activated, but I feel that in some cases it’s better not to use them at all! It’s just my personal opinion!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.