This post was last edited by huaguiyi on 2011-1-18 16:11Deputy Director: On-duty Shift Dispatcher
Members: Primary responsible persons from each operating area, as well as personnel from the Production Section, Technology Section, Safety Section, Mechanical & Equipment Section, and on-duty shift dispatchers.
Dispatcher phone number:
Dispatch desk: 8
General dispatch phone number:
Responsibilities: ① Upon occurrence of a power outage incident, activate the emergency response plan for power outages ; ②Members of the command team (except the heads of various operation areas) are to gather in the control room ; ③Convey various orders issued by the command center, and be responsible for coordinating emergency rescue efforts in different operation areas during accident responses ; Upon receipt of the call, responsible for directing the activation of various systems. ④Organize and coordinate matters related to seeking external assistance, and be responsible for reporting the accidents ; ⑤Responsible for reporting the status of the gas holder to the head office. For each 2-meter drop in the level of the 3 gas tanks, it is necessary to report to the company’s headquarters ; When it is necessary to lower 3 gas holders onto their beds, a report must be submitted to the company’s general dispatcher in advance. II. In the event of an emergency power outage, the following actions shall be taken according to the system areas: ★Distribution system: Emergency operations within the distribution system area are carried out by the distribution operation team, which forms an emergency incident command team: Team leader: Head of the distribution operation team; Responsibilities: Responsible for overall emergency management in the distribution operation area. Deputy Team Leader: Safety Operations Supervisor. Responsibilities: Responsible for ensuring safety in emergency situations within the transmission and distribution operations area, as well as for overseeing production processes. Deputy Team Leader: Equipment Shift Supervisor. Responsibilities: Responsible for the operation and safety assurance of production equipment in the transmission and distribution operation area. Members: The shift supervisor and team leaders on duty. Responsibilities: Responsible for confirming operations on site. When the chief supervisor is absent, the safety supervisor assumes all of the chief supervisor’s responsibilities, with the remaining duties following in this order. Post-accident assembly point: Control room on the third floor of the blending station. Telephone:
I. Emergency operations at the blending station: Under normal circumstances, the capacity of a 50,000 m³ gas holder should not be less than 30,000 m³, and that of a 100,000 m³ gas holder should not be less than 60,000 m³. 1. Immediately open Mixing Valve #13 to maintain positive pressure in the external network. Responsible person: The on-duty staff at the blending station. 2. If gas is currently being vented from the gas holder, immediately close the vent valve. Responsible person: The on-duty staff at the blending station. 3. Verify that the inlet and outlet valves of both gas tanks are in the open position, while valves No. 1 for direct flow and No. 8 for high pressure are in the closed position, to ensure positive pressure in the external pipeline network as well as in the gas pipelines of the blast furnace and coke oven. Responsible person: The on-duty staff at the blending station. 4. Set the switch on the operating box in the gas holder pump room to the manual position, and close the oil inlet valve of the pump room. Responsible person: The on-duty staff at the blending station. 5. Close the inlet and outlet valves of the fan. Responsible person: The on-duty staff at the blending station. 6. If the personnel on duty at that time were undergoing routine inspections inside the cabinet, they should organize others to use manual rescue devices to bring out the people inside the piston, or use hand levers to rescue those trapped in the elevator car. If someone is inside the elevator car, turn off the power to the control room and move the car to the emergency stop position. If the car was located close to the landing door at the time, evacuation should be carried out directly through the landing door ; If the floor door is far away, the cabin door can be opened, and one can climb down the ladder inside the elevator shaft to reach the floor door and evacuate. After the people have evacuated, use a manual handle to move the cabin to the ground floor. Responsible person: The on-duty staff at the blending station. 7. One hour after a power outage, activate the backup fuel tank; if power is still not restored after one hour of using the backup tank, open the gas holder to release the gas inside it and carry out an emergency shutdown procedure. Responsible person: The on-duty staff at the blending station. 8. After a power outage, whenever the level of each of the two gas tanks drops by 2 meters, the on-duty staff must report this to the control room, which in turn reports it to the group company’s main control center. 9. Before the gas tank is lowered to the floor, the duty officer must report to the control room in advance; upon receiving this notification, the control room shall promptly report to the group company’s headquarters. Responsible persons: On-duty staff at the blending station, and on-duty dispatcher at the coking plant. II. Emergency operations at the pressure station: Under normal conditions, the capacity of the 50,000 M3 gas tank should be at least 30,000 M3. 1. Ensure that the inlet valve, release valve, and direct connection valve No. 2 of the 50,000 M3 tank are closed, while the outlet valve of the tank is open, so that gas can be supplied to residents as usual. Responsible person: On-duty staff at the pressure station. 2. Set the switch in the gas holder pump room control panel to the manual position, and close the valve of the oil inlet pipe in the pump room. Responsible person: On-duty staff at the pressure station. 3. If the compressor is currently in operation, close the inlet and outlet valves of the compressor. Ensure that the inlet valve, vent valve, and 2# direct-through valve of the gas tank are closed, while the outlet valve is open; then open the 3# direct-through valve. Responsible person: On-duty staff at the pressure station. 4. If this occurs during the routine inspection time at the machine location, personnel should be organized to use manual rescue devices to free those trapped on the piston inside the cabinet, or to use hand cranks to rescue those trapped in the elevator car. If someone is inside the elevator car, turn off the power to the control room and move the car to the emergency stop position. If the car was located close to the landing door at the time, evacuation should be carried out directly through the landing door ; If the floor door is far away, the cabin door can be opened, and one can climb down the ladder inside the elevator shaft to reach the floor door and evacuate. After the people have evacuated, use a manual handle to move the cabin to the ground floor. Responsible person: On-duty staff at the pressure station. 5. After a power outage, close the inlet and outlet valves of the compressor, and ensure that the valves at the end of the users using cutting gas are also closed. Responsible person: On-duty staff at the pressure station. 6. One hour after a power outage, activate the backup fuel tank; if power is still not restored one hour after the backup tank is used up, open the gas holder to release the gas inside it and carry out an emergency shutdown procedure. Responsible person: On-duty staff at the pressure station. 7. After a power outage, whenever the level of the civil gas tank drops by 2 meters, the on-duty staff must report this to the control room, which in turn shall report it to the group company’s main control center. 8. Before the gas holder is lowered onto the bed, the operator on duty must report to the dispatch room in advance. Upon receiving the notification, the dispatch room promptly reports it to the general dispatch center of the group company. Responsible persons: On-duty staff at the pressure station, and on-duty dispatcher at the coking plant. III. Emergency operations for pipeline groups: 1. Quickly proceed to the mixed-gas users to check and confirm whether they have closed the end valves, ceased gas usage, and to check for any gas leaks or unauthorized venting. Responsible person: On-duty staff of the Pipeline Team. 2. If it is winter and the temperature is low, after a power outage of 1 hour, close the main valve for the heating steam, drain water from the lowest point, and close the valves of the liquid discharge pipes one by one; then drain the water from the drains after 2 hours to prevent them from freezing damage. Responsible person: On-duty staff of the Pipeline Team. 3. Wait for instructions to prepare for valve cutting and gas supply. Responsible person: On-duty staff of the Pipeline Team. IV. After a power outage, all shift personnel shall set the transfer switches of the operating equipment to the zero position. V. Emergency tools: emergency lights, flashlights, fire extinguishers, fire axes, CO alarms. ★ Coke oven system: Emergency operations within the coke oven system area are carried out by the Coking Operations Area. The Coking Operations Area has established an emergency accident command team: Team Leader: Chief Coking Supervisor. Responsibilities: To be in charge of all emergency-related tasks within the Coking Operations Area. Deputy Team Leader: Safety Operations Supervisor. Responsibilities: Responsible for ensuring safety in emergency response efforts within the coking operation area. Deputy Team Leader: Technical Operations Supervisor. Responsibilities: Responsible for directing emergency production processes in the coking operation area. Deputy Team Leader: Equipment Operator. Responsibilities: Responsible for the operation of production equipment and ensuring safety in the coking operation area. Member: On-duty foreman. Responsibility: Responsible for confirming on-site operations. When the chief supervisor is absent, the safety supervisor assumes all of the chief supervisor’s responsibilities, with the remaining duties following in this order. Post-accident assembly point: Coking Central Control Room. Telephone:
I. Emergency operations for coke ovens:
1. In advance, connect a U-tube to the main blast furnace gas pipeline near the exchanger end, and place it outside the exchanger for standby use. Responsible person: Head of the coke oven fitter team. 2. In the event of a power outage, quickly cut off the power supply, press the manual button of the corresponding solenoid valve as indicated by the travel indicator, and operate the hand pump to move the exhaust gas travel pointer to the middle position. Responsible person: On-duty switch operator. 3. Observe the pressure in the U-tube; if the pressure is zero or slightly positive, personnel should promptly enter the basement, close all blast furnace gas cocks, introduce heating coke oven gas, and carry out gas shutdown and heat preservation measures. Responsible person: On-duty switch operator. II. Emergency procedures for coal delivery trucks: Responsible person: The driver on duty for the coal delivery truck. 1. After turning off the power to the coal truck, return the master controller to the zero position. 2. Quickly remove the guide sleeve pull rod pin so that the guide sleeve is lifted automatically under the action of the weight. 3. The two individuals pried open the brake, manually turned the wheel, and at the same time used a crowbar to move the running wheels, thereby pushing the coal cart away from the fire area. III. Emergency operations for the coke pusher: Responsible persons: the driver on duty for the coke pusher and the employee responsible for unloading coke on the machine side. 1. Turn off the power to the coke pusher and return the main control lever to the zero position. 2. Switch the pusher rod drive mechanism to manual mode, release the brake, and pull out the pusher rod; if it cannot be moved, the assistance of a crane operator is required. 3. Use the same method to shake out the leveling rod. IV. Emergency operations of the coke baffle car: Responsible persons: The on-duty driver of the coke baffle car and the on-duty coke-removal workers on the coke side. 1. Turn off the power to the quench car and return the main control lever to the zero position. 2. Remove the coke from inside the guide grid and near the furnace column. 3. Hold down the manual release button for the focus grid lock to deactivate the lock ; Hold down the manual button of the guiding grid solenoid valve to retract the guiding grid. 4. Push the coke car away from the fire zone. V. Emergency operations for the coke quenching vehicle: Responsible person: The driver on duty for the coke quenching vehicle. 1. Turn off the power to the coke quenching vehicle and return the main control lever to the zero position. 2. If the coking car is not positioned directly in front of the coking stack, activate the door-opening lever, place the red coke on the ground, and inform the fire truck to extinguish the coke ; If the coking quench vehicle is located in front of the coking stack, the fire truck can be notified immediately to carry out quenching. 6. After a power outage, the transfer switches of operating equipment at all posts must be set to the zero position. VII. Emergency resources and needs: 1. Basement: emergency lighting, fire extinguishers, fire axes, CO alarms, homemade wrenches. 2. Four essential items: fire extinguisher, handles for various manual devices, emergency lighting, pliers, hammer, adjustable wrench, and crowbar. VII. External Conditions: 1. The 100,000 M3 gas holder should be able to supply blast furnace gas to the blast furnace as soon as possible. 2. After closing the high-gas cock in the basement, open or close the flap valves on the two main pipes on the coke side as appropriate. ★ Chemical production system: Emergency operations within the chemical production system area are carried out by the purification operation area, which has established an emergency incident command team: Team leader: Head of purification operations; Responsibilities: Responsible for overall emergency management in the purification operation area. Deputy Team Leader: Head of Purification Safety Operations. Responsibilities: Responsible for ensuring safety in emergency situations within the purification operation area, as well as overseeing production processes. Deputy Team Leader: Shift Supervisor of Purification Equipment. Responsibilities: Responsible for the operation and safety assurance of production equipment in the purification area. Member: On-duty foreman. Responsibility: Responsible for confirming on-site operations. When the chief supervisor is absent, the safety supervisor assumes all of the chief supervisor’s responsibilities, with the remaining duties following in this order. Assembly point after an accident: Chemical Production Control Room. Phone number: I. Operation of the condensation unit: 1. First, close the outlet valve of the circulating ammonia water pump; responsible person: the employee on duty at the condensation unit. 2. Then, close all outlet valves of the operating pumps. Responsible person: The on-duty staff member of the condensation unit. II. Operation of the crude benzene unit: 1. Immediately close the main gas valve and the branch valves of the tubular furnace; responsible person: the on-duty employee of the crude benzene unit. 2. Immediately close the regenerator steam inlet valve at the same time; responsible person: the shift leader of the crude benzene unit. 3. Then close all outlet valves of the operating pumps; responsible person: the on-duty staff of the crude benzene unit. III. Operation of the scrubbing unit: 1. First, close the outlet valve of the rich liquid pump. Responsible person: The on-duty staff member of the scrubbing unit. 2. Next, close the outlet (inlet) valve of the benzene washing tower; responsible persons: the staff on duty in the washing unit and the shift supervisor. 3. Then close all outlet valves of the operating pumps; responsible person: the on-duty staff of the washing unit. IV. Ventilator Unit: 1. Close the ventilator outlet valve and the pressure booster inlet and outlet valves; responsible person: the on-duty staff of the ventilator unit. 2. The operator sets the switch on the aspirator operation box to the zero position. Responsible person: On-duty staff of the inspirator unit. V. Operation of the deacidification unit: 1. Open the bypass of P-6401 and close the side-stream valve. Responsible person: The shift supervisor of the deacidification unit. 2. Next, close the on-site valve of the Claus furnace and the external steam valve; responsible person: the first member on duty in the deacidification unit. 3. Then close all outlet valves of the operating pumps; responsible person: the second crew member on duty in the deacidification unit. VI. Control Room Unit: 1. The control room shall coordinate with the coke oven to ensure that the flap for adjustment cannot be closed, while simultaneously keeping a close eye on the pressure in the deacidification tower. Responsible person: The on-duty staff in the control room. VII. System startup: 1. Wait for the dispatch instructions to start the circulating ammonia water pump. 2. Commence construction in accordance with the sequence once the conditions are met. VIII. Potential risks: 1. If the process runs for too long, sulfur recovery may become blocked. 2. If the temperature of the Kohler furnace is below 800 degrees, automated ignition is required. 9. After a power outage, all switchgear for the operating equipment at various stations must be set to the off position. X. Emergency tools: Emergency lights, flashlights ★ Operations system Emergency operations within the operations system area are carried out by the Operations Work Area. An emergency accident command team has been established in the Operations Work Area: Team leader: Chief Operations Supervisor Responsibilities: Responsible for all emergency-related tasks in the Operations Work Area. Deputy Team Leader: Operations Equipment Foreman
Responsibilities: Responsible for equipment operation and safety assurance during emergency incident handling in the operations area. Members: On-duty foreman, on-duty team leader. Responsibilities: Responsible for confirming on-site operations. When the Chief Shift Supervisor is absent, the Equipment Shift Supervisor shall perform all duties of the Chief Shift Supervisor, and this order shall be followed accordingly. Assembly location after an accident: Comprehensive Pump Room. Phone number: I. Emergency procedures for the Comprehensive Pump Room: 1. The water level in the reservoir of the Comprehensive Pump Room should be maintained above 2.5 meters on a daily basis. Responsible person: Staff of the comprehensive water pump room. 2. The on-duty foreman and two male workers responsible for water treatment immediately proceeded to the integrated water pump room, where they worked together to sequentially shut off the make-up water valve of the reservoir, two outlet valves for production and fire-fighting water, the outlet valve of the clean circulating water pump, the outlet valve of the chilled water pump, and the outlet valve of the chilled water circulation pump. Waiting for power to be supplied. Responsible persons: the shift supervisor, two male workers on duty for water treatment, and the personnel on duty at the comprehensive pump room. 3. After power is restored, the shift foreman, the male water treatment worker, and the personnel at the integrated water pump room sequentially open the makeup water valve of the reservoir, two outlet valves for production and fire-fighting water, the outlet valve of the clean circulating water pump, the outlet valve of the chilled water pump, and the outlet valve of the refrigeration circulating water pump. Responsible persons: the shift supervisor, the two male workers in charge of water treatment on duty, and the employees on duty in the comprehensive pump room. 4. After receiving the call, other units shall resume production in accordance with the operational standards for their respective positions. Responsible person: The on-duty staff of the operating system. II. After a power outage, all personnel at each post shall set the transfer switches of operating equipment to the zero position. III. Emergency resources: Emergency lights, flashlights ★ Storage and transportation system Emergency operations within the storage and transportation system area are carried out by the Storage and Transportation Operations Area. An emergency incident command team has been established in this area: Team leader: Chief Supervisor of Storage and Transportation Duties: Responsible for all emergency-related tasks in the Storage and Transportation Operations Area. Deputy Team Leader: Head of Storage and Transportation Safety Operations. Responsibilities: Responsible for ensuring safety in emergency situations within the storage and transportation operations area, as well as for overseeing production processes. Deputy Team Leader: Operations Supervisor of Storage and Transportation Equipment. Responsibilities: Responsible for the operation and safety assurance of production equipment in the storage and transportation area. Member: On-duty foreman. Responsibility: Responsible for confirming on-site operations. When the chief supervisor is absent, the safety supervisor assumes all of the chief supervisor’s responsibilities, with the remaining duties following in this order. Meeting point after an accident: Jiaotai post control room. Phone number: I. Emergency procedures for the storage and transportation system: 1. Observe the condition of the red coke at the Jiaotai post observation area; if necessary, contact the control room or call 119 directly to have fire trucks sent to extinguish the red coke there. Responsible person: The employee on duty at the Jiaotai post. 2. Personnel assigned to the coke handling system conveyor belts must immediately inspect the conveyor belts in this system. If any red-hot coke is found on the belts, it must be promptly removed. In case of a fire on the belt, it should be extinguished immediately using a fire extinguisher or other appropriate means. After that, inspections must continue until power is restored and the conveyors resume normal operation. Responsible person: The on-duty employee of the conveyor belt system at Jiao Shang. 3. The operator at the crusher station should set the crusher switch to the zero position. The employee on duty at the Coal Belt 4 station should go to the crusher station to verify that the crusher switch is indeed in the zero position. Responsible persons: Employees on duty at the crusher station, and employees on duty at the Coal Belt 4 station. 4. Other positions are on standby for this position. 5. If the power outage lasts until shift change, the shift must be handed over on the post. II. After a power outage, all personnel at each post shall set the transfer switches of operating equipment to the zero position. III. Emergency resources: Emergency lights, flashlights. ★Power supply shutdown/activation: The operation of shutting down or activating the power supply is carried out by the automated operation area. An emergency accident command team has been established in the automated operation area: Team Leader: Chief supervisor of automated operations. Responsibilities: Responsible for all aspects of emergency response in the automated operation area. Deputy Team Leader: Supervisor of Automated Equipment. Responsibilities: Responsible for operating the equipment and ensuring safety in case of emergency incidents in the automated operation area. When the Chief Shift Supervisor is absent, the Equipment Shift Supervisor shall perform all duties of the Chief Shift Supervisor, and this order shall be followed accordingly. Assembly point after an accident: 6KV high-voltage distribution room. Phone number: I. High-voltage distribution operations in the coking area: Assembly point after an accident: 6KV high-voltage distribution room. Phone number: 1) Organization: Person in charge: Head of the chemical production electricians team; Person responsible for the task: Shift supervisor; Personnel involved: Shift-based power distributors and electricians. 2) Emergency measures: (1) Power shutdown: ① Set the switches for the suction machines, mixing stations, air compressors, feedout cabinets, and gas storage and distribution stations to the off position. ② For the integrated water transformer, suction pump transformer, phenolic cyanide transformer, coke oven transformer, and coal-coke transformer, as well as for crushers No. 1 and No. 2, set the forward and reverse operation switches to the off position. ③Confirm that all the circuit breakers in the high-voltage switchgear trolley have been opened. If a busbar isolator is found to be in the closed position, manually operate it to open. ④The on-duty electrician went to the mixing station to check whether the handcars of fans No. 1 and No. 2 were in the off position. ⑵Power supply: The utility worker performs the following operations: ① Supply power to the main water transformer. ②, deliver phenylcyanine transformers. ③, deliver coke oven transformers. ④Send the ventilator and coal coke transformer level by level. ⑤, to the feedout cabinets of the air compressor station and storage and distribution station. ⑥Low voltage is used first for lighting. ⑦The on-duty electrician went to the distribution rooms at the comprehensive water system, the vacuum pump unit, and the phenol-cyanide area, as well as the high-voltage room in the mixing station, to check whether everything was operating normally. (3) Emergency tools: Emergency lights, flashlights.
II. High-voltage power distribution operations in the material yard area:
(1) Organization:
Person in charge: Head of the material yard electricians’ team
Post supervisor: On-duty shift leader
Personnel: On-duty electricians and on-duty power distribution workers
Assembly point after an accident: High-voltage power distribution room in the material yard
Telephone:
(2) Emergency measures:
① After a power outage, shut down each 6 kV distribution circuit in the following order. The power outage only affects the fuel switch. Note: Operations on the 6KV incoming line and bus circuit are prohibited. ② After power supply is restored, wait for instructions from higher authorities; once power is supplied, proceed with the operations in the following order. ③ The on-duty electrician is responsible for operating the low-voltage circuits in each substation. Principle: Restore using the original power supply in operation. First, restore the various low-voltage incoming circuit breakers, and then engage the busbar circuit breaker. Check the PLC system and various low-voltage distribution circuits. ④ If the DC panel is not functioning, all operations of the high-voltage system must be carried out manually. (3) Emergency tools: Emergency lights, flashlights.
III. Operation of the instrumentation system:
(1) Organization:
Person in charge: Head of the Instrumentation Team
Post supervisor: Shift supervisor
Personnel: On-duty instrumentation maintenance staff
Assembly point after an incident: Central control room of the chemical production plant
Telephone:
(2) Emergency measures:
(1) Power outage
① First, go to the coke oven area and coordinate with the operators on duty to adjust the flow control dampers for the gas supply to the 8 blast furnaces and coke ovens to appropriate positions and lock them in place. Use the manual lever to control the draft in the flue until the draft is appropriate. ②Go to the chemical production control room to assist the process engineers in checking the liquid levels in the waste boiler and sulfur condenser. Cooperate with process engineers to carry out the verification of control valves. ⑵Power supply: Coordinate with the personnel on duty in accordance with the sequence of process startup, and follow the instructions of the dispatchers. ㈢ After a power outage, ensure that the opening degree of the regulator valve behind the suction pump is above 50%. ㈣. After a power outage, the gas suction control flap is in the normally open position. (v) The automatic flap on the main blast furnace gas pipeline cannot be closed after a power outage. ㈥ Emergency tools: Emergency lights, pneumatic actuators, manual levers. IV. DCS system operation: ㈠ Organization: Responsible person: Head of the instrumentation team; Person in charge of the post: Shift supervisor; Staff: On-duty instrumentation maintenance personnel; Meeting place in case of an accident: Chemical production control room; Telephone number: ㈡ Emergency measures: 1. Emergency measures for UPS power supply: Immediately monitor the UPS power supply at the site once a power outage occurs; shut down the DCS system as soon as a power failure alarm is triggered. 2. Emergency measures in case of power failure of the DCS system: ① Shut down the APM cabinet at the GUS station and then cut off the power supply. ②At the GUS station, turn off HM and NIM SHOUT DOWN one after another. ③Power down the GUS station hosts one by one. ④, turn off the UPS power supply. 3. Emergency measures for restoring power to the DCS system: ① Activate the UPS power supply. ②Power on the APM. ③, Power on HM (HM will start automatically). ④Power on the NIM cabinet; once the address is correct, wait for the installation to proceed. ⑤Start the GUS station; once the HM is powered on, download the NCF file from the HM to the GUS station. If HM cannot start, use the quick-start disk to start GUS. If GUS fails to start, reinstall the system software and application software. ⑥After the GUS station is powered on, NIM is downloaded from the GUS station. ⑦After normal communication via NIM, the program files are downloaded from the GUS station to the APM. (III) Emergency tools: flashlight, emergency light, system software, application software. V. After confirming that power supply to all systems is normal, report to the control room promptly. III. Requirements for various operation areas and relevant departments in the branch factory: 1. Once the emergency plan is issued, each operation area must conduct training for all its employees on the procedures for emergency responses within that area, and organize practical drills in the near future. The Mobile Operations Department shall be responsible for overseeing and inspecting these drills in collaboration with the relevant functional departments. 2. Regarding emergency resources and tools (such as manual devices for elevators and hoist cages), the Motorization Section shall organize relevant functional sections to conduct spot checks. In the event of a sudden power outage, the coking plant formulates specific implementation plans based on specialized knowledge and system requirements, organizes personnel effectively, minimizes losses, and restores production as quickly as possible. ★Requirements for other plants: ① When a power outage occurs, the users at each plant must immediately close the mixed gas valves at their respective locations to maintain a positive pressure in the pipelines. ②In the event of a sudden power outage, the gas compressor will stop operating, and the steel mill must immediately close the valves at the users’ points where cutting gas is supplied. ③In the event of a sudden power outage, the delivered household gas is supplied to the users due to the pressure inside the cabinet. ④When supplying power, give priority to powering the coking plant. ⑤In the event of a sudden power outage, fire trucks are needed to provide support and protection on the side of the coke oven.