Fluctuation issue in electromagnetic flowmeter readings

2011-01-19View Original

Thread Content

Recently, while debugging a project, I found that the electromagnetic flowmeter installed was showing extremely volatile readings, sometimes reaching 50% of its full scale. After checking for a long time, it was discovered that the liquid used for testing empty vehicles was deionized water, which caused this result. The problem was solved after switching to tap water. Therefore, when there is a problem with an electromagnetic flowmeter, the first thing to check is whether the fluid meets the design requirements. A little lesson to share with everyone.
Reply #22011-01-19
In 3Q, fluids determine everything. .
Reply #32011-01-20
Ah! But sometimes, those in the manufacturing field can’t argue their way out of it!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.