2011-01-22View Original

Thread Content

Just starting to work with ESD. According to information found online, it is an emergency stop system. But the design is such that a row of buttons and switches all require signal verification by the DCS cards before the DCS interlock program can be executed. Question 1: Is this still considered ESD? According to information found online, it is generally said that ESD does not pass through the DCS, but the DCS can only monitor the status of ESD events.
Reply #22011-01-22
What you described doesn’t seem to be ESD; it might be a hardware console for DCS
Reply #32011-01-23
It seems like you’re saying that logic is executed in the DCS. In the case of true ESD signals, they go directly to the ESD system, and the signals within the ESD system are generally transmitted to the DCS for monitoring. You can take a look at the wiring diagram.
Reply #42011-01-23
ESD is a hardware-independent system and should not be included in the DCS. What you’re referring to seems to be the auxiliary control panel.
Reply #52011-01-27
You keep talking about the auxiliary control panel, hehe~~
Reply #62011-01-27
You must be referring to the auxiliary control panel. Generally, DCS and ESD systems are two independent systems; however, the two systems may be connected through communication or direct wiring. In our plant, the ESD and DCS signals are such that field signals are transmitted through one-input two-output safety barriers (for analog signals) or relays (for digital signals), thereby enabling the transmission and control of a single signal across two systems.
Reply #72016-04-27
Hello, could you please send me your contact information? I am inquiring about ESD control systems
Reply #82016-05-17
1. Maybe you mistook the item and got it mixed up. 2. Perhaps the system is small, so it’s not cost-effective to use ESD; therefore, the DCS takes on all the tasks. Personal opinion, for reference only
Reply #92016-05-18
What you're doing here with ESD on DCS is generally not allowed; the safety level and scanning speed of DCS do not meet the requirements for ESD! It’s best to do them separately
Reply #102019-11-04
According to IEC 61508 and 61511, ESD is a separate system, and the control console is an independent console for the ESD system.
Reply #112019-11-04
It does not count as ESD; ESD must be independent, including the circuitry for the cards as well as the instruments and valves. It cannot be connected to ESD via DCS. The operation of ESD can be transmitted to the DCS through the network

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.