I would like to ask the experts here: how can the water hammer problem in dry steam pipes be solved?

2011-02-09View Original

Thread Content

This post was last edited by wang*neng on 2011-2-14 at 15:16 :dizzy: The heat exchanger of the drying fan has a very high steam heat transfer capacity; the steam return pipeline contains a high amount of water, which leads to severe water hammer effects. As a result, the steam return pipe of the heat exchanger vibrates greatly, and the pipelines suffer frequent damage. I would like to ask manufacturers how to deal with this issue. Installing a steam trap at the return main pipe did not prove effective; the steam flow rate for each radiator is 6 tons per hour, while the steam trap installed has a capacity of 20 tons per hour – yet this still did not resolve the vibration issue!
Reply #22011-02-14
The drain valve should be of the type that discharges water as soon as it appears, and it should be installed at the lowest point of the piping network. As long as the condensate water can be drained promptly, water hammer generally will not occur. The above opinions are for reference only

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.