Urgent help needed with a CS3000 issue.

2011-02-23View Original

Thread Content

Question 1. I saw that when others were programming, they used %sw0004 in a sequencer table to set the SIO instrument block to aut mode. I know it’s customized by the system, but I don’t know what it means. I hope experts can answer. Question two. I have created many sequential empty tables, but I have to manually switch to automatic mode every time I run a simulation. I would like to know how to enable automatic mode automatically. I saw a post before suggesting that another sequential empty table be created, but what I don’t understand now is that the sequential empty table created in this way is still in manual mode, right?
Reply #22011-02-23
Reply 1# coolfires117 ST16 or LC64 is fixed: manual; set to AUT after creation is complete. This is to prevent unexpected jumps when you write out the sequence table and download it to FCS. The system’s built-in MAN gives you time to verify the system. Was it saved when you exited the simulation? If it is not stored, ST16 or LC64 will still be MAN; it must be manually set to AUT for the next simulation
Reply #32011-02-23
There is another way to remain in automatic mode, which is to write a program using a computation block. It is not recommended in general; it can be used when there are few programs. It is still recommended to use sequential control for automation.
Reply #42011-02-23
What does %sw0004 mean?
Reply #52011-02-24
This post was last edited by jlshnlhj on 2011-2-24 at 11:05. There are various ways in which the processing timing can be set for a sequential control table: “Choose either ‘Periodic Execution Type (T),’ ‘One-shot Processing Type (O),’ ‘Startup at Initial Cold Start/Restart (I),’ or ‘Restricted Initial Execution Type (B).” “...I saw a post earlier suggesting that another sequential control table should be created; that is, create such a table with a processing timing setting of I. In its Action settings, set those other sequential control tables that need to operate automatically to automatic mode as well. As for %SW0004, just check the IM manual – it’s just an ordinary switch. The manual describes it as follows: A4-10 ■ System Common Switches: The PFCS/SFCS common switches (element numbers: %SW0001 to %SW0200) are designed as system switches with fixed functions. Users can check the status of these common switches. The data related to the common switches %SW0004, %SW0005, and %SW0031 is entered by the users themselves. The common switches %SW0097 to %SW0200 are valid only when the extension common switch is set to 1 (valid).”
Reply #62011-02-24
Reply to 5# jlshnlhj: Thank you for your help. I still have one question – I saw that in other projects, the pbs5c module is used to create a pop-up interface for controlling the motor’s automatic and manual mode as well as its start and stop functions. What does this module mean? I’ve tried hard for a long time but still can’t figure out how to use it.
Reply #72011-02-24
This post was last edited by jlshnlhj on 2011-2-24 13:34. Check the IM manual: CS 1000 CS 3000 Reference Function Block Details (IM 33S01B30-01E). If you read it carefully and patiently, you’ll be able to understand it. D4-41 D4.8 Extended 5-Push-Button Switch Block (PBS5C)
Reply #82011-03-02
Reply to 6# coolfires117: The PBS5C or PBS10C instruments that I understand are those that combine several internal switches in one panel; each button seems to be adjustable, allowing it to be pressed simultaneously with multiple switches or just one switch. In one project I worked on, product selection was involved, with a choice of 5 options out of 1, and this module was used for that purpose. Take a look at the M materials; what I said isn’t very detailed either.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.