2011-03-05View Original

Thread Content

Our low-temperature cryogenic LPG pumps are used only once every few days. What precautions should be taken when starting the pump again? Were the inlet and outlet valves fully closed after the last pump shutdown? What will be the consequences if everything is turned off?
Reply #22011-03-05
When starting the pump, it is necessary to vent air; after stopping the pump, the inlet valve should be closed. If both the inlet and outlet valves are closed and high temperatures occur, the pressure of the liquefied gas can rise sharply due to its properties, which can lead to explosions. However, if the outlet valve is open and there is a safety valve on the outlet pipeline, an explosion will not occur.
Reply #32011-03-05
Reply 1# lovestory: After stopping the pump, close all inlet and outlet valves, and relieve pressure from the pump. Ventilation should be performed before starting the pump.
Reply #42011-03-05
Close the inlet and outlet valves completely to relieve pressure from the pump. That’s how we are.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.