Under normal circumstances, is a 900-pound oxygen valve required for a 6.5MPa gasification furnace? Is the pressure too high?

2011-03-09View Original

Thread Content

This post was last edited by security on 2011-3-9 at 17:26. I would like to ask the forum members: is it generally necessary to use 900-pound oxygen valves for 6.5MPa gasification furnaces these days? Is the pressure too high?
Reply #22011-03-09
900psig= 62.05barG
Reply #32011-03-09
For pipelines under 6.5 MPa pressure, it is advisable to use valves with a pressure rating of 10.0 MPa or higher
Reply #42011-03-09
The 900lb mentioned by the poster likely refers to the nominal pressure, and it is not 900psig = 62.05barG
Reply #52011-03-09
Under normal conditions, the operating pressure is 6.5 MPa, and 600 LB is sufficient to meet this requirement. The operating temperature under the conditions mentioned by the poster must be above 150 degrees; based on the properties of the material, only a 900LB grade can be used to meet these requirements. So, the original poster, it was right for the colleague in process engineering to make this choice
Reply #62011-03-10
I cannot agree with what was said upstairs! Valve selection should be fine; the medium temperature can’t exceed 100 degrees Celsius, based on experience. . .
Reply #72011-03-10
1 pound is approximately 0.45 kilograms, so 900 pounds equals 405 kilograms. The pressure must be quite high, right?
Reply #82011-03-10
You can’t calculate it that way upstairs; the American system has several pressure levels, and if you want to find out more, take a look at HG20615-2009
Reply #92011-03-11
Could you explain it in more detail? Thank you!
Reply #102011-03-11
According to HG20615, 900 pounds corresponds to a pressure of 15 MPa; therefore, your piping system should use a pressure rating of 600 pounds (11 MPa) or 10 MPa. In China, it is common to choose pipe fittings with a slightly higher rating, so it’s also acceptable to use 900 pounds or 16 MPa

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.