Monitoring and remote operation of waste heat boilers: Where should the PLC be placed?

2011-04-11View Original

Thread Content

The waste heat boiler requires monitoring and operation on-site, and the main control room located 500 meters away also needs to be able to monitor and operate it. Is it more appropriate to place the PLC on-site or in the main control room? How can it be made more economical and practical?
Reply #22011-04-11
Build a separate control room on-site (it doesn’t need to be very large), and then transmit the signals to the DCS via communication interfaces such as RS485 (the interfaces must be compatible). As for displaying on the DCS, it requires cooperation between the PLC (which provides communication and parameters) and the DCS manufacturer to achieve this.
Reply #32011-04-12
Reply to 2# sun_fm: I agree quite a bit with what you said; I think it’s appropriate to hold it on-site!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.