Is there any inverter installed in the control room?

2011-04-15View Original

Thread Content

I would like to install the frequency converter in the MCC room, integrating it with the MCC. However, our management team, who have a mechanical background, insists on installing it in the control room, arguing that the control room is equipped with air conditioning while there is no need for air conditioning in the MCC room. They also claim that this is how it was done at the foreign-owned company Vauxhall before. Has anyone else done it this way? Aren’t you afraid of distractions?
Reply #22011-04-15
That leader is truly a leader. Speechless! Saving costs is going too far! I’ve been working for over a decade now, and I’ve really never seen an inverter installed in the control room.
Reply #32011-04-15
Electrical is in charge; it’s not our concern regarding the instruments{:1_90:}
Reply #42011-04-15
It’s not electrical, but from what I remember, I’ve never seen inverters in the control room
Reply #52011-04-15
Our frequency converters are installed on-site as well as in the power distribution room.
Reply #62011-04-15
I want to know this answer too; when we were handling installations before, the manager mentioned this solution
Reply #72011-04-16
This post was last edited by liuei on 2011-4-16 at 12:43. Inverters generate strong EMC interference, so it is not suitable to install them in the control room!
Reply #82011-04-16
LZ is related to electrical appliances; we don’t understand instruments. . .
Reply #92011-04-18
I think frequency converters should not be placed in the control room; the main concern is signal interference. Also, does the inverter require air conditioning? All the frequency converters I’ve seen are placed on-site or in the power distribution room, without any air conditioning installed.
Reply #102011-04-18
Reply to 6# shyg0813: How was it actually installed later on?
Reply #112011-04-18
What a shame! What a shame!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.