We have a Rosemount 3051S transmitter here, and the pressure readings are low during the day but high at night. Why is that? ? ? ? I earnestly request advice from all the experts. Urgent! ! !
Is it due to the temperature? Check the transmitter.
I really don’t know; I’ve never heard of such a problem. Please, experts, help to analyze it
Check the instruments first. If the instrument is fine, then it’s related to the medium being measured. I think it has something to do with the measuring medium; generally, the pressure is high during the day and low at night.
Is there a pressure guide tube? Sometimes, fluid accumulates in the pressure guide tube at night, and evaporation during the day can also cause similar phenomena.
Is the medium you are measuring a gas with high volatility and a low boiling point? At night, when the temperature is low, a liquid column forms in the pressure guiding tube, while during the day, when the temperature is high, it evaporates! !
It might be due to temperature; this can cause fluid to accumulate in the pressure guide tube at night, and evaporation during the day can also lead to similar phenomena
What we are measuring is chlorine gas. Since it is to be used in a chain reaction, we installed two pressure transmitters at the same location; the problem occurred with one of them, while the other one remained stable.
Use the elimination method; switch the wiring for the two transmitters. Alternatively, try using a different transmitter; it seems that the issue is caused by interference or the location mentioned upstairs. Please take action on this, and I look forward to receiving your solution along with the reasons behind it.