Regarding the low outlet pressure interlock in the vacuum furnace

2011-05-03View Original

Thread Content

Regarding the low outlet pressure interlock in the vacuum furnace, the interlocks triggered by low inlet flow rate and high outlet temperature both result in the shutdown of the gas valve for the main burner, thereby preventing dry burning or coking. However, in addition to the shutdown of the main burner valve, the interlock triggered by low outlet pressure also causes the feed valve and the furnace outlet valve to shut down as well. I don’t understand why this is the case. I would appreciate it if experts could help explain this. Thank you
Reply #22011-05-03
Reply 1# man19501: In my opinion, such a interlock should be one for detecting leaks in the furnace tubes; If the furnace outlet temperature is too high, it is sufficient to shut down the fuel supply via interlock; shutting down the feed supply is not acceptable. Continuing or increasing the feed supply can help lower the furnace outlet temperature ; This is not appropriate; you need to discuss and study it thoroughly with the design team
Reply #32011-05-03
Reply to 2# linweihua6: Thank you for your answer; this explanation is quite reasonable. Thank you again
Reply #42011-05-03
I agree with the opinion above: the gas supply is cut off in case of a fault, but the feed supply remains active to prevent the furnace tubes from being damaged by high temperatures. This is also related to the design of the wind-on and wind-off valves – the gas valve is a wind-on valve, while the feed air valve is a wind-off valve.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.