Why does it switch to automatic mode when the water supply pressure is low?

2011-06-13View Original

Thread Content

Our plant has 7 30MW boilers with a header system; the feedwater pressure is low. Why should the feedwater automation be disabled?
Reply #22011-06-13
The feed water pressure is low, there is a lot of interference, and the automatic feed water control is unstable; therefore it has been switched to manual mode
Reply #32011-06-13
When the water supply pressure is low, the opening degree of the control valve is already quite high, and it has moved outside the optimal automatic adjustment range. It is recommended to investigate the cause of the low water supply pressure; it is likely that there is a problem with the water pump itself
Reply #42011-06-13
Automatic water supply control is carried out based on factors such as water level and steam flow; it doesn’t seem to take inlet water pressure into account for protection purposes, right? Is there something wrong with this programming?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.