Can the equipment grounding be connected to the lightning protection down conductor? ? ?

2011-06-22View Original

Thread Content

As the title suggests~~~ Could any fellow sailor provide the answer? It would be great if there’s **standard support**! ! !
Reply #22011-06-23
This post was last edited by fangqiong on 2011-6-24 at 16:14. If you are referring to the static grounding of equipment, then it is not allowed. According to Article 3.6.3 of the «Code for Design of Static Grounding in Petrochemical Industries», «The following grounding main lines shall not be used for static grounding: Case 4 – Lightning protection down conductors».

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.