2011-07-09View Original

Thread Content

On the return water pipeline for the burner cooling water, there is a safety valve in front of XV0719 (the return water cut-off valve). Its setting pressure is 6.2 Mpa. What is the purpose of this safety valve? ?
Reply #22011-07-09
Reply 1# liuyanguo2010: Due to the interlocked shutdown of the burner cooling water system, the inlet and outlet valves for the burner cooling water will be automatically closed. That safety valve is there to prevent the burner’s cooling water coil from being damaged; high-pressure gas escaping from it is prevented by this safety valve.
Reply #32011-07-09
I agree with what was said on the second floor; however, the pressure of the cooling water for the burners in the space furnace is higher than that in the vaporization furnace. If there is a leak in the burner coils, the cooling water will leak into the vaporization furnace. That’s why the cooling water system for the burners in the space furnace does not have safety valves.
Reply #42011-07-09
Reply to 2# mozhiyang: After the safety valve activates, gas will leak into the vapor-liquid separator for the return water of the burner’s cooling system; that is a device operating at atmospheric pressure
Reply #52011-07-10
Is it a safety valve designed to prevent overpressure caused by the vaporization of the burner cooling water, with the inlet and outlet valves for that water fully closed?
Reply #62011-07-10
Reply to 4# liuyanguo2010: How could it leak from the gas-liquid separator? The safety valve is installed in front of the cut-off valve at the burner cooling water outlet.
Reply #72011-07-10
Reply to 6# mozhiyang: That’s right, you’re correct. But after the safety valve activates, the flow is directed to behind the outlet shut-off valve.
Reply #82011-07-10
This post was last edited by sangeshuiyuan on 2011-7-10 18:12. The safety valve should be set at a pressure higher than that at which the vaporizer starts to operate!
Reply #92011-07-10
Reply to 6# mozhiyang: The safety valve bypasses the valve that supplies cooling water to the burner, allowing gas to enter the burner’s cooling water gas-water separator and thus return to the incineration system from the top!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.