Thread Content
Are instruments used in the safety control of synthesis systems? If this can be achieved, netizens, could you let me know! Thank you.
What type of synthesis process? Could you give a detailed introduction?
Small-scale ammonia synthesis plant, equipped with a radial synthesis tower.
1 Alarm for high temperature on the wall of the synthesis tower 2 Temperature control of the synthesis tower 3 Alarm for high differential pressure in the ammonia synthesis tower 4 Alarm for high differential pressure in the ammonia synthesis system 5 Online analyzer for fresh hydrogen 6 Online analyzer for recycled hydrogen 7 Control and interlock of the hydrogen-to-nitrogen ratio 8 Automatic adjustment of the ammonia liquid level 9 Alarms for high and low levels of the ammonia liquid level 10 Automatic adjustment of the coolant level 11 Alarms for high and low levels of the coolant level 12 Automatic adjustment of the waste heat boiler liquid level 13 Alarms for high and low levels of the waste heat boiler liquid level 14 Remote control of the recycled gas flow rate 15 Automatic adjustment of the waste heat boiler steam pressure 16 Alarms for high and low levels of waste heat boiler steam pressure 17 Alarm for high pressure in the ammonia cooler 18 Alarm for high pressure in the liquid ammonia storage tank 19 Installation of safety valves (in waste heat boilers, ammonia coolers, water coolers, etc.) 20 Installation of emergency vent valves 21 Provision of emergency spraying facilities in the liquid ammonia storage area 22 Installation of an emergency shutdown device or system 23 Installation of detectors for flammable and toxic gases