Zirconia in tubular heating furnaces

2011-10-21View Original

Thread Content

This post was last edited by linweihua6 on 2011-11-2 at 19:47. Guys, I know the purpose of installing zirconia in the flue of tubular heating furnaces, but why is zirconia also installed at the junction between the convection chamber and the radiant section?
Reply #22011-10-21
1. Is it for comparison, to see if there is secondary combustion?
Reply #32011-10-21
Reply to 2# haijiang417: Please explain in detail
Reply #42011-10-21
There is no secondary combustion! The oxygen content in the two areas is basically the same; secondary combustion! The oxygen content in the upper part is lower than that in the lower part – just my opinion! For reference only! Hehe!
Reply #52011-10-21
Previously, to measure the oxygen content in the flue gas, oxygen analyzers were installed on the flue after convection. In fact, the quality of combustion depends mainly on the oxygen content in the radiation chamber. There may be air leakage at the door of the elbow box in the convection section; as a result, the oxygen content in the flue gas after convection is not accurate. Therefore, modern oxygen analyzers are generally installed at the radiant ceiling, which allows for a more accurate assessment of the combustion conditions.
Reply #62011-10-21
We added an air preheater later on. The chimney of the reduced-pressure furnace does not emit any flue gas; instead, the flue gas from this furnace is combined with that from the atmospheric-pressure furnace and exchanged heat in the air preheater. As a result, the flue gas damper of the reduced-pressure furnace remains closed at all times. Due to the temperature difference, a suction force is created, and it is impossible to keep the flue gas damper completely closed; air is drawn into the furnace. Therefore, the oxygen concentration measured at the upper part of the radiation section is lower than that measured in the flue gas, and it is also more accurate

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.