Ask a question about the wiring of a thermal resistor

2011-10-25View Original

Thread Content

This post was last edited by zyzs on 2011-12-4 08:39. The platinum resistance sensors use a two-wire connection, while the PLC ports use a three-wire connection; is it necessary to use a three-core cable in order to make a proper connection? ? ? ? ? How do I connect?
Reply #22011-10-26
The thermal resistor is a three-wire type, so of course it has three wires
Reply #32011-10-26
Thermistors come in two-wire, three-wire, and four-wire types. The resistance of the two-wire cable itself can interfere with the measurement results; in three-wire and four-wire systems, a bridge is used to compensate for the cable resistance, resulting in more accurate measurement outcomes.
Reply #42011-10-27
Two-wire PT100: In many cases, two-core wires are used to connect directly to the PLC port, and a shorting wire is then used to connect the other port of the PLC to it
Reply #52011-10-27
The connection cable does not have to be three-core; a two-core cable will also work. Using a three-core cable eliminates the impact of wiring resistance on measurements, resulting in higher accuracy compared to using a two-core cable.
Reply #62011-10-27
Thermal resistors are generally three-wire types; during wiring, two of the wires are connected together
Reply #72011-10-27
A three-wire system is more accurate, as it eliminates the influence of wire resistance on the measurement results. It must be a three-core cable.
Reply #82011-10-27
Just twist the two together, and connect the other one separately
Reply #92011-10-27
The resistance of three-wire circuits has a significant impact on measurements; 3 ohms corresponds to nearly 10 degrees. This effect is not noticeable at high temperatures, but three-core cables should still be used at low temperatures.
Reply #102011-10-29
Three-wire wiring is commonly used for thermistor connections.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.