Division of I/O points between ESD and DCS

2011-11-10View Original

Thread Content

I’m now facing issues with pump control; the pump’s signals are already sent to the ESD system. Is it still necessary to have hardwired connections in the DCS to display the pump’s status and to control its shutdown?
Reply #22011-11-10
If there are terminal blocks that can handle two connections, that would work, but it’s better to use communication for this purpose; we have already implemented both wired connections and communication solutions
Reply #32011-11-10
It is possible to divide into two by using an isolation safety barrier
Reply #42011-11-10
Reply to 2# nihaocarter: Oh, then how many points are required to enter each of your systems? When entering the DCS here, one of the pump DI values is actually 3.
Reply #52011-11-10
Reply to 2# nihaocarter: What about the other aspects? For the hardwired connections to ESD, how is it handled for those connected to DCS? Is it through communication or some other method? I hope experts can give some advice.
Reply #62011-11-10
Reply to 4# jml11: The points related to ESD are all critical points of the equipment; the DCS is used to record trends, while the communication-related aspects can be handled casually
Reply #72011-11-11
On our side, if a pump is connected in series with four points in total, there are two feedback signals from the DCS and one DO signal, while there is one DO signal from the ESD system; they are all wired together in series. Action ESD takes priority, causing the entire circuit to be shut off in a cascade manner. DCS operates by opening the valves provided that there is no cascade ESD that would prevent the circuit from remaining powered; therefore, cascading connections are quite common.
Reply #82011-11-11
We all use separate signals with one input and two outputs via safety barriers.
Reply #92011-11-11
We all use separate signals with one input and two outputs via safety barriers.
Reply #102011-11-11
We all use separate signals with one input and two outputs via safety barriers.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.