Regarding the rectifier stop interlock issue

2011-12-08View Original

Thread Content

This post was last edited by sunjl1981 on 2013-1-6 at 21:52. If the rectifier stops, KV231 and KV241 switch, with KV241 turning on and KV231 turning off. If the KV-231 and KV-241 interlocks are disconnected while the rectifier is stopped. So will it become KV231 turned on and KV241 turned off? Also, when the rectifier supplies power, will KV231 and KV241 switch automatically? # + + . hcbbs
Reply #22011-12-09
First of all, it must be understood that when the KV-241 is in the open position, power cannot be supplied to the electrolyzer. The opening of the KV-241 is an interlock condition for the single-cell interlock of the electrolyzer; since this interlock condition is met, how is it possible to supply power?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.