Question regarding pre-coating of circulating water
Thread Content
Hello, dear sea friends. I have only been working for a few years; I’ve participated in the construction of several projects. However, in those previous projects, no pre-coating was used for the circulating water – instead, hydroxyl oxidation was employed, with an oxide film forming during operation. I am now taking on another project that uses a traditional circulating water system, and pre-coating is required. I wonder if, during this pre-coating process, all the equipment in the factory that relies on circulating water cannot be operated? That is what is known as cold-state pre-coating. Mainly, I am preparing a start-up schedule, and I want to carry out the trial operation of the air compressor along with the chemical cleaning of the circulating water system and the pre-coating process. I wonder if it’s feasible?---|---|---
Circulating water volume (Q) | m3/h | 42,000
Wastewater discharge volume (B) | m3/h | 500
Evaporation volume (E) | m3/h | 600
Water loss due to wind and leakage (L) | m3/h | 100
Makeup water volume (M) | m3/h | 1,200
System water storage volume (V) | m3 | 16,000
Concentration ratio (N) | — | 1.5–2.5
Circulation rate (A) | % | 96.9
II. Full analysis of the quality of the makeup water for the system is shown in the table below:
Serial No. | Analysis Item | Unit | Result
---|---|---|---
1 | pH value | — | 7.69
2 | Mg2+ | mg/L | 98.45
3 | Turbidity | NTU | 4.2
4 | Cl– | mg/L | 235.38
5 | Conductivity | us/cm | 5,640
6 | SiO2 | mg/L | 4.35
7 | Phenolphthalein alkalinity | mmol/L | 0
8 | Total dissolved solids | mg/L | 2,556
9 | Total alkalinity | mmol/L | 3.61
10 | Total iron | mg/L | 0.83
11 | Total hardness | mmol/L | 10.84
12 | Total phosphorus | mg/L | 0.04
13 | Ca2+ | mg/L | 284.62
14 | SO42+ | mg/L | 1,864.3
15 | Na+ | mg/L | 0.96
16 | HN4+•N | mg/L | 12.37
17 | K+ | mg/L | 0.45
18 | Al3+ | mg/L | 0.29
III. Organizational responsibilities:
1. Water supply and drainage department:
(1) In accordance with the requirements of the cleaning plan, it is necessary to verify that all components of the circulating water system, such as chemical dosing devices, acid dosing devices, wastewater discharge valves, makeup water valves, online pH meters, and flow meters, can meet the needs related to chemical addition, acid addition, wastewater discharge, and makeup water supply during cleaning. If these components do not meet the requirements, temporary measures must be taken, such as adding additional makeup water and wastewater discharge pipelines, as well as more chemical dosing and acid dosing equipment ; (2) Coordinate with the technical staff from the cleaning and pre-coating manufacturers to resolve various issues that arise during the cleaning and pre-coating processes ; (3) Adjusting the amount of water required for circulation and storage during cleaning and pre-coating processes, carrying out water supply and drainage tasks, as well as operating the chemical dosing and acid addition devices in the circulating water system ; (4) Carry out proper safety supervision and inspections. 2. Production Technology Department: The scheduler is responsible for coordinating the various factories, instructing them to put all the equipment and pipelines in the circulating water systems into operation, and ensuring that all parameters are controlled as specified in the plan. Meanwhile, the laboratory carries out analyses and tests in accordance with the requirements of the plan. 3. Supply and Sales Department: Responsible for notifying the manufacturers of cleaning and pre-coating services to provide an adequate amount of chemicals as required by the plan, and arranging technicians to be on site to guide the cleaning and pre-coating process. 4. Manufacturer responsible for cleaning and pre-coating: (1) The manufacturer’s technical staff should arrive at the site in advance, familiarize themselves with the conditions there, and ensure that the pumps used for adding chemicals and acid are sufficient to meet the requirements for cleaning and pre-coating. Make specific arrangements for the chemical addition ports, acid addition ports, and storage areas for chemicals, and determine the locations for monitoring probes and sampling points together with your company’s technicians ; (2) A chemical cleaning and pre-coating analysis room should be set up in a room equipped with water, electricity, and other facilities that meet the requirements for water quality chemical analysis; standard reagents should be prepared, and the analysis instruments should be calibrated. In accordance with the project and frequency requirements outlined in the plan, assign monitoring and analysis personnel as appropriate, and install and test equipment for adding chemicals and acids ; (3) The on-site project supervisor shall arrange for proper safety measures during cleaning operations. All personnel involved must comply with the safety regulations during construction as well as various rules and procedures set by Henan Longyu Coal Chemical Industry; they must also receive safety training and be familiar with the relevant safety protection measures. III. Cleaning Procedure 1. Chemicals to be used: WT-301 cleaning agent, WT-309 defoamer. 2. Concentration of chemicals: 1000 ppm for WT-301 cleaning agent. 3. Method of addition: Shock addition. 4. Operation time: 10 hours. 5. Amount of chemicals required: (V + M × 10h) × 1000 ppm. Amount of WT-301 cleaning agent required (kg) = —————————— / 1000 = (12000 + 800 × 10) × 1000 / 1000 = —————————— = 20000 kg = 20 tons. In the formula: V – Volume of water in the system, in m3 ; (The minimum safe water level is approximately 12,000 m3) M – System water replenishment rate, in m3/h. (The water replenishment rate is approximately 800 m3/h). The consumption of WT-309 antifoam agent is 30 ppm; its addition should be adjusted according to the operating conditions of the system, with an estimated consumption of 400 kg. In the formula: V —— amount of water stored in the system, m3 ; (The minimum safe water level is approximately 12,000 m3) M – System water replenishment rate, in m3/h. (The water replenishment rate is approximately 800 m3/h.) 6. Operating method and end-point determination: Reduce the circulating water level to a safe low level; adjust the pH value of the circulating water using sulfuric acid to between 5.5 and 6.5. After about 1 hour for uniform distribution, gradually add the WT-301 cleaning agent. During operation, pay attention to the changes in various water quality indicators; test the pH value and turbidity of the circulating water every 2 hours. When the turbidity in the circulating water stops increasing, it indicates that the cleaning is complete. Throughout the cleaning process, attention should be paid to whether foam forms in the circulating water; if there is an excessive amount of foam, WT-309 antifoaming agent should be added promptly. After cleaning is complete, increase the water supply and drainage to change the water. The entire cleaning process is expected to take about 10 hours. 7. Monitoring: The reference standard is the \"Standard of China Association for Engineering Standardization\", with standard number CECS103:99. Specifically, the corrosion rate for carbon steel should be ≤3 g/m2•h, while the corrosion rate for copper and stainless steel should be ≤0.3 g/m2•h. IV. Pre-coating (I) Preparation work: 1. After chemical cleaning, pre-coating treatment should be carried out as soon as possible to prevent the heat exchange surfaces and water flow pipes from being corroded by dissolved oxygen in the water ; 2. Pre-film conditions: (1) The turbidity of the circulating cooling water should be <20 mg/L, and the total iron content should be <1 mg/L. High turbidity in the water or a high level of iron ions can affect the quality of the membrane. (2) Ca2+ ≥ 50 mg/L. Generally speaking, an important factor in the pre-coating process is the presence of sufficient calcium; when the Ca2+ level in the water is between 100 and 200 mg/L, the pre-coating effect is good. When the Ca2+ level is below 50 mg/L, CaCl2 should be added. (3) Sufficient pre-coating agent; (4) Appropriate amount of H2SO4. Controlling the pH value during the pre-coating process is one of the most important factors. The optimal pH value for film formation of WT-302 is 5.5–6.5 ; The film-forming effect declines when PH > 7.5 ; When PH > 8, the tendency for calcium phosphate deposition increases, affecting the density of the membrane as well as the binding force between the membrane and the metal surface ; When PH < 5.5, the polyphosphorus complex film will be solvated and destroyed. (5) At temperatures >15°C, the WT-302 pre-coating agent facilitates film formation when the cooling water temperature is high; in cases where it is difficult to increase the cooling water temperature, it can operate at room temperature. (6) Flow rate: During the pre-coating process, a slightly higher flow rate is appropriate, around 1.0~1.5 m/s. A high flow rate facilitates the diffusion of the pre-coating agent and dissolved oxygen in water; simultaneously, it promotes the electrodeposition process, allowing for an increased film formation rate and the creation of a uniform and dense film. However, if the flow rate is too high (greater than 2.5 m/s), it may cause the pre-coating solution to erode the metal through scouring. (7) Residence time: Due to the hydrolysis or degradation of polyphosphates in the system, a longer pre-coating time is not necessarily better; an excessive residence time can lead to the formation of calcium phosphate scale deposits. Normally, 24 hours after pre-coating, the pH value returns to its natural level; it is necessary to add a dispersant at a certain concentration to the system in order to prevent the deposition of calcium phosphate scale and zinc salts. (8) Monitoring: Pre-treated test pieces are attached to the hanging device in the tower tank for monitoring. The evaluation of the pre-coating effect can be carried out using the following methods: a) Visual inspection method: In the case of an excellent pre-coating effect, there will be a uniform colored film on the test pieces, or they will emit a blue light and exhibit a metallic luster, with no pitting. Depending on the pre-coating agent used, the color of the film formed on the test pieces varies. b. Copper sulfate solution method: Weigh 15 g of CaCl2 and 5 g of CuSO4, dissolve them in 100 ml of distilled water, and drop this solution onto the pre-coated test pieces; simultaneously, determine the time it takes for red spots to appear on the test pieces. It should be greater than 10S. (II) Start of pre-coating: Pre-coating involves using chemical methods to create a dense protective film on the surface of the equipment, thereby preventing direct contact between the heat exchange surface and the circulating water. This enhances the equipment’s corrosion resistance and ensures effective water treatment. Therefore, the equipment must be pre-coated. 1. Chemical to be used: WT—302 pre-coating agent 2. Dosage concentration: 300 ppm 3. Method of application: Shock dosing 4. Operation time: 30–36 hours 5. Amount of chemical required: (V + M × 36h) × 300 ppm. Amount of WT—302 pre-coating agent required (kg) = —————————— 1000 / (12000 + 800 × 36) × 300 = —————————— = 12240 kg = 12.24 tons. In the formula: V – Volume of water in the system, in m3 ; (The minimum safe water level is approximately 12,000 m3) M – System water replenishment rate, in m3/h. (The water addition rate is approximately 800 m3/h.) 6. Operating method and end-point determination: Operate the circulating water at a safe low level; adjust the pH value of the circulating water to between 5.5 and 7.5 using sulfuric acid, and gradually add the WT-302 pre-coating agent to the water intake tank. During operation, the pH value of the circulating water and the concentration of the WT-302 pre-coating agent are tested every 2 hours, and test pieces are used to monitor the effect of pre-coating; when a stable multicolored pattern appears on the surface of the test pieces, it indicates that the pre-coating process is complete. At this point, an appropriate amount of WT-304E scale and corrosion inhibitor should be added for dispersion purposes, in order to prevent the formation of calcium phosphate precipitates in the system; meanwhile, the volume of water added and removed should be increased, and the water should be replaced. 7. The high-concentration pre-coating solution in the system should be removed from the circulating cooling water system as quickly as possible; once the water quality meets the requirements of the operating process, the addition and removal of water should be stopped, and the system will then operate normally.