For 380V motors, the operating current is unbalanced; what is the acceptable range for three-phase imbalance? ? ? ? How to choose ammeters and CTs for motors below 10kw
Reply #22012-02-14
The three-phase deviation current of the motor should be within 5% to be considered normal. When selecting an electric motor ammeter, it is necessary to consider the motor-driven equipment and its rated current; generally, a pointer-type ammeter is used. It is appropriate for the rated current to fall between 1/2 and 2/3 of the ammeter’s scale. The selection of the CT should match that of the ammeter (for example, if the ammeter is selected as 100/5, then the CT should also be 100/5).

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.