2012-02-19View Original

Thread Content

The UPS has been in operation for a year, and it is now time for maintenance. Has the battery pack not been discharged for a long time? How should the discharge operation be carried out? What are the technical requirements? Are there any specialized devices for discharging battery packs?
Reply #22012-02-19
A crude method: cut off the power supply and discharge it with an appropriate load.
Reply #32012-02-19
We generally follow the instructions, applying it once a month; this is specified in the relevant equipment maintenance procedures.
Reply #42012-02-20
When we want to discharge it, we connect the battery to an electric furnace for discharge.
Reply #52012-02-21
No special equipment is required; just one or two full charge and discharge cycles are enough. Check the status of the UPS before making a decision
Reply #62012-02-21
Actually, discharging is very simple – just turn off the main circuit. The main thing is that the discharge current must be limited: for example, when using a 100AH battery, the discharge current should not be less than 10A; it is recommended that it not exceed 40A, as otherwise it will have an adverse effect on the battery, though it will not affect the main unit. At the same time, since the condition of the battery is unknown before the discharge test, it is recommended to turn off only the input to the main rectifier circuit during discharge, while keeping the input to the electronic bypass intact. The specific procedures can be followed according to the instructions or operating guidelines
Reply #72012-02-21
It’s quite fresh, haha. May I ask how it’s done exactly?
Reply #82012-02-22
This method works! Could you give more specific details?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.