Problems with the signal wires of electric and pneumatic valves

2012-02-26View Original

Thread Content

There is currently a 4-wire electric control valve in use, with one set of signal wires and one set of 220V power wires. I want to replace it with a pneumatic control valve. Can the existing signal wires be connected directly to the new pneumatic valve?
Reply #22012-02-26
The poster wants to use this set of signal wires after replacing the pneumatic valve, right? There should be no problem; they are all 4–20mA signals
Reply #32012-02-26
Of course, no problem. Ah, they are all standard current signals
Reply #42012-02-26
No problem, they are all 4 to 20MA signals!
Reply #52012-02-27
Oh, I see. Thank you all, seniors. Should the original 220V power cable be removed then? Is there any danger in staying?
Reply #62012-02-27
The original power cable should first be powered off, and its ends should be wrapped with insulating tape to ensure safety; of course, it’s even better to remove the cable altogether!
Reply #72012-02-27
If all the signals are 4–20mA standard signals, then there’s definitely no problem. It is best if your electric valve and the new pneumatic valve are at roughly the same height; in other words, the length of the signal cable needed to connect to the connector on the pneumatic valve’s actuator should be sufficient. It is best to remove the original power cable; if not, the power should be turned off and the cable covered with insulating tape. In case of need.
Reply #82012-02-27
The wires can be used, but the type of clip needs to be changed.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.