How to choose a 1250 transformer busbar?

2012-02-27View Original

Thread Content

For a 1250KVA transformer, how should the busbars on the 400V low-voltage side be selected? Current: 1250 / (1.732 * 0.4) = 1804 A. Should the busbar be selected as TMY 120*10 (with a current-carrying capacity of approximately 2160 A at 40°C)? Is that suitable?
Reply #22012-02-27
The specifications you chose are quite acceptable. But in practical applications, it’s better to leave some margin. It is recommended to consider TMY 2*80*8 for reference.
Reply #32012-02-27
Thank you. I’ve left a 360A margin – is that not enough? 2 (80*8) has 100A more than the 120*10 I chose; if it were you designing it, would you choose 2 (80*8)? I’m a beginner; please give me some advice. Also, for the neutral busbar, can I use a 60*8 one? It was chosen based on half of the current-carrying capacity of my main busbar – is that appropriate? Another question 1: If one of the outlets in a cabinet has a load of 150 KW, I have chosen a circuit breaker with a frame rating of 400A and a rated current of 320A ; Is a 300/5 current transformer a suitable choice for me? The ammeter was also chosen to be 300A – could this be too low? Question 2: For the main circuit breaker on the low-voltage side of the 1250KVA transformer, I have chosen the RDW1C-3200M/3P/2500 model from Renmin Electric (an intelligent universal circuit breaker) with a rated current of 2500A. Is this appropriate? What if we choose a rated current of 2000A? Question 3: When selecting isolators for low-voltage distribution cabinets, is it necessary to choose load isolators? How should an isolating switch be selected for a 600A load? I used to work in automation; I’ve just started working on electrical design now, and there are so many issues. Thank you for your guidance!
Reply #42012-02-28
1. Choose the 80*8 model with zero emissions. 2. At a load of 150 Kw, the ammeter reads 500 A, and the current transformer is also 500/5A. 3. For the incoming line, the starting current of the total load plus the maximum load must be taken into account; therefore, a 2500A rating is required. Too small is unreliable. 4. For 150Kw, choose a circuit breaker of 320A; for a knife switch, 400-500A is also suitable. It is better to be large rather than small.
Reply #52012-03-02
The last edit to this post was made by Baghdad on 2012-3-2 at 14:00. Considering the dimensions, spacing, and margin of the transformer’s low-voltage terminals, as well as the convenience of installation, using 1*100*10mm copper strips that meet national standards is sufficient. The busbars are generally short, with sufficient capacity. The most important advice is to measure the width of the low-voltage terminals; it’s best to use copper plates that are 100 mm wide for installation.
Reply #62012-03-02
This post was last edited by Baghdad on 2012-3-2 22:57. The main feed line does not require the use of isolating switches; drawer-type 2500A circuit breakers are reliable and practical. For lower-level switches, knife switches are used for isolation when the current is below 600A, while drawer-type circuit breakers are preferred for currents above 600A, as they offer reliable and effective protection.
Reply #72012-03-03
A 600A drawer circuit breaker is quite expensive compared to ordinary circuit breakers, right? Are you referring to the universal type? Should I choose a type B ordinary circuit breaker? Install a 1000A isolating switch at the front.
Reply #82014-07-21
.................................
Reply #92014-07-21
Just finished a project: a 1250 transformer, TMY 2*80*8 busbars, with N and PE wires being TMY 80*8. Intelligent universal circuit breakers of 630A and above are referred to as molded case circuit breakers hereafter.
Reply #102014-07-22
3×2(100×10) + 1(100×8). Refer to the atlas 03D201-4: Layout of 10/0.4kV transformer rooms and installation of common equipment components in substation facilities; on the last page, look at the options regarding the low-voltage side outlets of transformers. Alternatively, consult the Handbook for Industrial and Civil Power Distribution – it’s either in Chapter 2 or Chapter 3, and the information is there as well
Reply #112014-07-22
As a supplement regarding △-Y, 3×2(100×10) + 1(100×10)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.