2012-03-13View Original

Thread Content

Control valve, Siemens valve positioner; the valve starts to experience instability once its position exceeds 70%, while it operates normally when the position is below 70%. Let’s discuss the possible reasons for this phenomenon
Reply #22012-03-13
What type of valve is it? Try setting the control circuit to manual to see how it behaves, and then set the locator to manual as well to observe the situation.
Reply #32012-03-13
No breathing at manual operation, ruling out the issue of unstable DCS signals! The problem I was experiencing has been identified; it was due to a low air supply output from the valve actuator. Adjusting the knob on the actuator resolved the issue!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.