Thread Content
305-AT-0101 Understand the meaning of this code
305 Device Number, AT Analysis Instrument, 0101 Serial Number
The explanation is correct; 0101 can also be called a sequence number
AT: Strictly speaking, it is a component instrument, including online analysis of toxic gases, flammable gases, etc
A for alarm, T for transmitter; AT refers to combustible, toxic, and fire alarms – what follows should be the tag number
Agree with the person above; our company uses the same numbering system.
305 is the device, at is the analytical instrument, 0101 is the process number
This post was last edited by qugd on 2012-3-20 07:31. 305 refers to the unit or device number; AT stands for analyzer, and the signal is used for transmission purposes to the DCS or data acquisition unit (as opposed to alarm A, recording R, indication I, etc.). 0101 denotes the 0101st analyzer within that unit or device. Together, these three elements constitute what is known as the tag number. If there are several identical analyzers with the same function installed at the same analysis points for several identical devices or apparatuses within the same unit, then tag numbers such as 305-AT-0101A/B/C/D/…… are used to distinguish each analyzer.
I have nothing left to add! ! ! ! ! ! ! !
305 is the device number in the project, AT is the name of the instrument; it is an online analysis instrument used for detecting toxic/flammable substances, etc. The final digit represents the instrument’s location code
What Haiyou said on the 8th floor is absolutely correct and comprehensive! !