For a single 1250KVA transformer, would current quick-break protection, overcurrent trip protection, gas protection, and oil temperature alarm be sufficient as protections? How should the setting values for current quick-break protection and overcurrent protection be determined?
Overcurrent protection for transformers: (1) Set to avoid the maximum load current that the transformer may experience; (2) Set to avoid the maximum operating current resulting from automatic load switching under overload conditions; (3) Set to avoid the situation where loads are automatically connected to the transformer’s low-voltage busbar; (4) Set in coordination with adjacent protective devices. When the low-voltage side of the transformer is equipped with outlet protection, it should be coordinated accordingly. Current quick-break setting: 1. Calculate based on the maximum short-circuit current flowing through the protection during external short-circuit faults ; 2. Calculate based on avoiding the inrush current of the transformer (3 to 5 times the rated current of the transformer).
The setting values for overcurrent and quick-break protection, as well as their operating times, are specified in relevant regulations, and these values are determined based on the terminal impedance of the transformer; The protection setting values for transformers are generally determined by the power supply authority, so the poster doesn’t need to calculate them