Tricon AO card failure

2012-04-09View Original

Thread Content

The control system for one set of centrifuge units in our factory is Tricon; the LOAD light indicates a fault in the AO card, but all four outputs are functioning normally. Please help to resolve this issue
Reply #22012-04-11
Oh, just find a resistor of more than 250 ohms to short the unused AO channels on the terminal board
Reply #32012-04-11
It can’t be that the card itself is giving a false alarm, right? Are your output cards redundant? If so, you can try switching them to see if that helps. If it’s not redundant, then card testing should be carried out better when the device is shut down.
Reply #42014-12-02
I can help with TRICON replacements
Reply #52014-12-03
Replace the card assembly at the appropriate time to check if there are any issues; if there are problems, then examine the entire circuit. If no problems are found, it indicates that the original card assembly is faulty.
Reply #62018-05-02
Diagnose it using diagnostic software; voting errors usually occur in such cases

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.