The positions of the ground switch, isolating switch, and circuit breaker in the primary wiring diagram of the power system

2012-04-17View Original

Thread Content

In the schematic diagram of the primary power system (220kV system), it is generally the case that: ① there is a disconnect switch on each side of each circuit breaker, and ② ground switches should be present on both sides of each circuit breaker and disconnect switch. (Apart from the busbar-side isolator) Is my understanding correct?
Reply #22012-04-26
It should be the isolating switch first, the grounding switch in the middle (with upper and lower grounding contacts), and the circuit breaker last. Because the sequence for power outage is to first turn off the circuit breaker, then pull the isolating switch, and finally close the grounding switch.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.