Are there such requirements for instrument cables in explosion-proof areas?

2016-10-12View Original

Thread Content

Must the instrument cables in the tank farm be armored cables? Some experts came to inspect and said that our cables are unarmored and need to be replaced. It’s not mandatory to do so, but it is required that each cable be run in its own conduit; even within cable trays, each cable must be separated by conduits. I’m just an ordinary instrument maintenance worker – I’m not sure if there are any regulations regarding this Thank you all!
Reply #22016-10-12
Instrument cables are all low-voltage cables with shielding; it doesn’t seem there’s any requirement for them to be armored
Reply #32016-10-12
I’m not sure; if that’s really the case, then the workload would be enormous
Reply #42016-10-12
Where did these experts come from? Do the cables in the bridge frame need to be armored? ? ? Armoring is required for direct burial; what does it have to do with the tank area?
Reply #52016-10-12
Please have the experts present the relevant standards for everyone to study*.
Reply #62016-10-12
I have worked on various instrument projects for LNG irrigation areas, but I have never done this before.
Reply #72016-10-13
The standards do not specify such a requirement; only directly buried cables need to be armored. One can’t always follow what experts say.
Reply #82016-10-13
I’ve also never heard that armor is necessary
Reply #92016-10-13
What a ‘expert’ – you should just ask him which standard and which version it is
Reply #102016-10-14
Thank you all! I’ll go talk to the manager right away. {:2_31:}

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.