What is the priority order when the UPS loses mains power?

2018-05-03View Original

Thread Content

When the mains power supply from UPS is lost, one approach is to first switch to the battery; only after the battery’s charge is depleted is the bypass switched on; Another approach is to first switch to the bypass supply (the bypass and mains power usually come from different sources), and then switch to the battery. Which method is better? What is the switching sequence for UPS units of different brands? I know Power Pioneer is the first type; it seems Emerson is the second?
Reply #22018-05-04
We adopt a unified UPS system across the entire company: when the mains power fails, the UPS switches to batteries to continue supplying power, while simultaneously sending a power failure alert to the control room; the electrical team then checks the status of the UPS to determine whether it has switched to bypass mode.
Reply #32018-05-04
Under normal circumstances, the switching sequence of a UPS in the event of a power outage is as follows: battery – bypass – maintenance power supply

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.